Re: Multi-fuel boiler?
Posted: Tue Mar 02, 2010 6:09 am
A LP Gas (Propane) tank behaves very similarly to a steam boiler. The only difference is that the pressure-temperature relationship for Propane is different than the relationship for steam.
With a steam boiler, holding pressure of several atmospheres (say 100 PSIG), you can open a valve and let off steam. If there is no heat source to the boiler (no fire), then steam pressure will decrease, and eventually the boiler will reach one atmosphere absolute pressure( 0 PSIG, 212F, 100C), and no more steam comes out. If you want to have more steam come out, and you want to maintain any pressure, you have to add heat to the boiler. In the case of a steam boiler, this heat is supplied from the fuel/fire.
The Propane tank has the same type of relationship, except the propane tank will get well below 32F (0C) when the pressure reaches one atmosphere absolute ( 0 PSIG). At ordinary ambient temperature, the propane in the tank will be at several atmospheres pressure.
Normally the heat to keep the propane tank warm enough is ambient air heating the tank, typical ambient temperatures in the range of 60-80F (15-25C) .
However the heat available from the ambient air has limits. If you want to draw large quantities of propane from the tank, the ambient heat transfer to the tank is not enough, and the propane boils away at lower and lower temperature & pressure. Eventually the tank gets very cold, and the available rate of drawing off propane is very limited.
With a high capacity burner, you need to supply extra heat to the propane tank. One good method is to flood the tank with ordinary lake or sea water. This water is capable of supplying adequate heat to keep the propane near ambient temperatures, which gives an available propane pressure of several atmospheres. The maximum temperature that the propane tank can experience is only the lake (or sea) temperature, and the corresponding propane pressure is within the safe limits of the propane tank.
Another method mentioned earlier is to use a steam coil or hot water jacket surrounding the propane tank. This method allows the potential to overheat the propane tank, which raises the pressure above the safety limits of the propane tank. As previously mentioned, this method is wrought with danger, and should never be used.
[/img]